Ok, just a little help:

First time I've seen a transformer with a wire for "Shield". DO I just solder it to ground ?

https://secure.cedist.com/images/inv/p- ... wiring.gif

Thank for any help
0 x

CurtissRobin
Senior Amp Tech
Senior Amp Tech
Posts: 1169
Joined: Sat 08/09/08 2:00 am
Location: Columbia River Gorge, Oregon Side

Post by CurtissRobin »

That wire connects the Faraday shield to ground. The Faraday shield is there to divert noise to ground, keeping it out of the secondary circuit.

Here's a load of information about it if you have a strong desire to read more. http://www.powertransformer.us/isolatio ... ormers.htm

KennyO
0 x

stevesuk
Frequent poster
Frequent poster
Posts: 893
Joined: Sat 07/19/03 2:00 am
Location: UK
Contact:

Post by stevesuk »

The shield winding which is a single ended winding (only one connection) is also connected to earth for safety as well as an electrostatic shield.

It is usually between the mains or higher voltage and lower voltage winding. If there is a short or more correctly an earth (ground) fault, the shield carries the fault to ground and blows the fuse, rather than causing the potential on the lower voltage winding to rise dangerously.
If you have one (not all transformers do) you may as well connect it.

Steve UK

www.valvepower.co.uk
0 x

Zemaitis
Occasional poster
Occasional poster
Posts: 119
Joined: Tue 03/22/05 2:00 am
Location: Hawaii
Contact:

Post by Zemaitis »

Thank you for answering my question. I figured it was suppose to go to ground, but just wanted to make sure. And learning what it does and why is very informative.